forum.rcware.eu » MiniPLC (IPLC200/IPLC300) (english)

AEW21.1 and MiniPLC

  1. Jan Vidim
    rcware team

    When integrating the M-Bus AEW21.1 converters to MiniPLC beware of the timeout settings in the comm parameters of each datapoint (Special params - Telegram timeout): if there are communication problems, increase this value from default 400 up to 2000 ms.

    Posted 3 years ago #