    There have been requests lately asking for help with MiniPLC (same situation is with touchscreen process stations, anyway) alarm e-mail configuration. E-mailing did not work, although during tests in the office everything was OK.

    The problem was with SMTP server: the MiniPLC is connected to the Internet via a provider who is able to allow access to particular SMTP servers only to prevent spamming from within the network. Contact your ISP or network admin to get the necessary data:
    - name or IP address of the SMTP server
    - user name (if this is not an anonymous server - today, nearly all servers request authentification)
    - password for this user name
    - port which the server listens on
    - is the Secure Socket Layer (SSL) protocol used?
    Enter those data in the Project alarms configuration menu of the Touchscreen Editor.

    NB.: even RcWare Vision can send e-mails, you only have to use scripting. We will be pleased to send you a sample project, just drop a mail to support@domat.cz. What is it good for? For example, automatic energy readouts sent to the utility provider at the beginning of each month...